Author Topic: not able to conect to T100MD888+  (Read 10862 times)

cwollman

  • Newbie
  • *
  • Posts: 1
  • I'm a llama!
    • View Profile
not able to conect to T100MD888+
« on: January 25, 2010, 10:06:18 PM »
Hi
I just received this new T100MD888+ PLC and I got it set up and was trying some test programs. It was working fine for 3 programs I tried, but then when I was sending it the fourth program it came up with a error. I now can not communicate with it. I tried to do the reset procedure listed in the book but no luck.

Can any one help me.
Clarence

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:not able to conect to T100MD888+
« Reply #1 on: January 26, 2010, 01:24:28 PM »
If the program you sent to it is using the COMM Port for its own communication then it will interfere with the ability of the TLServer to transfer program to it.

Turn on DIP switch #4, the POWER OFF and ON to reset the PLC. Now it will not run any program and its COMM1 is set to 9600,8,1,n.

Now go to TLServer, open up the serial port setup and set the comm port to 9600 bps, 8,1,n. Try to communicate with the PLC by sending it an "IR*".  If successful it will respond with "IR01*". Then send it a blank program. You can turn off DIP switch #4, reset the PLC and change baud rate in TLServer back to 38,400.
Email: support@triplc.com
Tel: 1-877-TRI-PLCS