Internet PLC Forum
Welcome,
Guest
. Please
login
or
register
.
1 Hour
1 Day
1 Week
1 Month
Forever
Login with username, password and session length
News:
Home
Help
Search
Login
Register
Internet PLC Forum
»
General
»
Technical support
»
MDS100-BW 9600 Baud
« previous
next »
Print
Pages:
1
[
2
]
Author
Topic: MDS100-BW 9600 Baud (Read 34335 times)
Petty_boy
Jr. Member
Posts: 53
I'm a llama!
Re:MDS100-BW 9600 Baud
«
Reply #15 on:
July 15, 2009, 02:17:58 PM »
Hi Guys,
I'm still waiting for my 2424 to come back from repair but i would like to test the CPU's you sent over.
Can i use the TLserver and my RS485 convertor to test the baud @ 9600??
Marcus
Logged
support
Global Moderator
Hero Member
Posts: 3174
Re:MDS100-BW 9600 Baud
«
Reply #16 on:
July 15, 2009, 03:45:39 PM »
Yes, you certainly can. TLServer also can compute the FCS for you, just enter the command string excluding any FCS, and click the compute FCS button to get the FCS, then add that to the command string followed by "*" and press the Enter key.
Logged
Email: support@triplc.com
Tel: 1-877-TRI-PLCS
Petty_boy
Jr. Member
Posts: 53
I'm a llama!
Re:MDS100-BW 9600 Baud
«
Reply #17 on:
July 15, 2009, 04:02:37 PM »
Hi,
thanks for the reply.
Command string:- PRINT #3 "?P0203";"PROJECT ID 090009"
FCS = 4C
String:- PRINT #3 "?P0203";"PROJECT ID 090009" 4C*
Is that right??
Logged
support
Global Moderator
Hero Member
Posts: 3174
Re:MDS100-BW 9600 Baud
«
Reply #18 on:
July 15, 2009, 04:09:58 PM »
No, TLServer only supports the multi-point command. You do not put any of the TBASIC command. Only the text string itself.
E.g. Enter "@F0?P0102Testing" , click FCS button. It will return FCS=0C.
Now add 0C to the above string and the whole string is:
@F0?P0102Testing0C*
Press Enter key to send it to the display.
Logged
Email: support@triplc.com
Tel: 1-877-TRI-PLCS
Petty_boy
Jr. Member
Posts: 53
I'm a llama!
Re:MDS100-BW 9600 Baud
«
Reply #19 on:
July 16, 2009, 12:57:21 AM »
Ok thanks,
I'll give it a try and come back to you.
Cheers
Logged
Print
Pages:
1
[
2
]
« previous
next »
Internet PLC Forum
»
General
»
Technical support
»
MDS100-BW 9600 Baud