Yes, turn ON dip switch 4, reset the PLC, change TLServer settings to 9600 bps. Then transfer a blank program to it. Next, turn off DIP switch #4, reset the PLC, change TLServer baud rate settings back to 38400 and you should now be able to regain control of the PLC.