Modem Communication
« on: January 19, 2004, 11:50:27 AM »
 I have a remotely located M-Series PLC connected to a analog modem.
  I am able to connect from PLC to a telephone but whem I want to connect to PLC via Telephone line with a host PC I have not any sign from PLC .
  Any idea ?
 Thanks in Advance .
« Last Edit: December 31, 1969, 04:00:00 PM by 1076562000 »

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re: Modem Communication
« Reply #1 on: January 19, 2004, 08:52:29 PM »
You have to put your modem in "Auto Answer" mode so that when you PC dial your remote modem it will answer the phone and then connect itself to the modem. See the "Appendix 3: PLC to Modem Communication Setup" in your Internet TRiLOGI reference manual for more details.