I would like to build a zone controller for my boiler using the T100MD888+.  It has the right number but the wrong kind of I/O.  The entire system is 24VAC.  Is the EXP1616R my best solution for reading 24VAC inputs and controlling 24VAC devices?

thanks

Joel Moore

  • Full Member
  • Posts: 128
    • View Profile
Re:AC I/O
« Reply #1 on: October 30, 2006, 09:49:50 AM »
You could use external relays.

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3174
    • View Profile
    • Internet Programmable PLCs
Re:AC I/O
« Reply #2 on: October 30, 2006, 05:18:54 PM »
If you need 8 relay outputs and 8 relay inputs (to convert the AC signal to DC to the T100MD888+) , then you have to check if the cost of buy 16 external relays plus the wiring is worthwhile compared to the EXP1616R price of $160.00. EXP1616R gives you 16 relay outputs and 16 AC inputs directly.