Analog ground point for Nano-10
« on: June 10, 2025, 09:32:36 AM »
I am working with a Nano-10 to work with 4-20 mA sensors.

The Nano-10 does not appear to have an analog ground connection.  The best that I can do is connect the free end of the current sense resistor to my common DC bus.

I am concerned about minimizing noise pickup by the ADC circuitry.

Is there a spot on the Nano-10 that I could solder onto as an analog ground?

Gary Dickinson

support

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 3180
    • View Profile
    • Internet Programmable PLCs
Re: Analog ground point for Nano-10
« Reply #1 on: June 10, 2025, 10:00:47 AM »
Nano-10 does not have a separate analog ground. So yes you can connect the ground to the power supply 0V as the common ground. Ground noise has not been a problem for the typical applications that Nano-10 have been being used in the past. We do recommend connecting any additional 0.1uF capacitor across the analog input terminal to minimize fluctuation in the readings or do a software average of multiple readings.